2 AC Thor 9S in an off-grid system with 3 MP 48/5000 + 2 Fronius Symo 6.0-3

Hello everyone,
is anyone else running two My PV AC Thor 9S units in an off-grid system, and if so, how have you configured them?
Via Modbus TCP, i.e. by entering an IP address in the AC Thor, or purely via frequency-dependent control?
The three MultiPlus units only provide a total of 15 kW, while the Fronius units are supposed to provide the main share.
So my question is: if I let the Cerbo control it via Modbus, will it regulate things knowing that there are two Fronius units connected to the system, and later even three, or do I have to use frequency control only?
As I said, it’s an off-grid system.
Many thanks,
Gerald

In an island system, this currently only works via frequency.
You’ll then have to match the frequencies to each other.

Work is also under way to integrate My-PV into Opportunity Loads, which would allow control via Modbus, as far as I know.