1x MP-II 48/5000 ESS on L1 in 3-phase house, last check before I buy

After reading/lurking on the forums for a few months, I feel I have my design in order - discussed with my electrician, and the Click&Design website numbers seem plausible too.

But, since this is the first time for him building a system like this (his core business is rewiring old houses, not adding battery systems) I’d like to check on a few safety items based on your collective experience here. This will be a mostly DIY build, with all wiring checks and utility connections performed by the electrician for certification.

Attached my design that I sent to my electrician and supplier before.
In short it will contain:
MultiPlus-II 48/5000/70-50 230V
CerboGX + display
VM-3P75CT Energy meter
Lynx ditributor
SolarEdge SE6K 7.3kWp
NKON ESS 16kW battery

My main questions that are still open for double-checking:

  1. Fuse setup OK? Upgrade to the Class-T 250A at the battery for instance, as proposed by my electrician? And the NKON’s internal 250A fuse, 200A MEGA per Multi once the two future Multis arrive are also ok?
  2. I’ve read about the possible issues with incorrect numbers in VRM with a single Multi on L1 next to a 3-phase SolarEdge setup ( 1-Phase ESS on 3-Phase Grid with Phase Regulation: "Total of all phases", Error displaying correct consumption - VictronEnergy ). Anything else a beginner usually gets wrong in a similar setup?
  3. I feel I can better dig a new cable directly from the workshop to the utility closet for the 3P connection, as I’m not entirely sure how the current cable runs through/under the house. It should have become a separate line already during our last renovations, but I have no proof this actually was installed that way. Is there any way I can check for that? (I know this is better asked of my electrician, but am interested in your experience - it would be a ~20m cable that in future needs to carry the full house load)

Hello and a warm welcome to the forum :waving_hand:

Whatever other tips and suggestions may come along …

I would definitely add a PV component to this system that will continue to work during a grid outage. So either an AC PV component on the Multi’s AC Out (a single-phase PV inverter) or a DC PV component via an MPPT. Perhaps you have roof space, or room on the façade or carport, to expand the PV system.

Otherwise, the drawing already looks great … I’m sure plenty more suggestions and tips will follow …

You have done your homework, but there is no pv energy meter, you need that to measure solar output (i could be wrong but dont think solaredge can communicate with the gx)

Also you wont have battery backup this way when grid fails nothing is connected to ac out

If your plan is to upgrade to 3 phase in the future you need to have additional multiplusses in the same build range (year/hw revision)

For system design questions you need to go to your victron dealer, this community is not for those specific questions

There have been many complaints about SE PV inverters on the forum, I would do some digging on the site just so you go into this fully informed.
The seamless and well-travelled route is ideally Fronius.

Thank Steffen, Marc and Nick, both for your welcome and your feedback.

The main goal of this setup is to raise my self-suffiency in the evenings now (the Dutch saldering rules changw in a few months), while preparing for a system that can take over during outages.

I am aware that the current setup doesn’t fully support that yet. The main issue is the SolarEdge: it shuts down without the grid, and running it on the Multi’s AC-out is reportedly not very stable. I hope to avoid most of the connectivity issues reported here with a modbus proxy: HomeAssistant holds the one connection to the SolarEdge, and the Cerbo reads via the proxy. To really keep the solar working during an outage I’d need anoter ~2k of components which is a budget issue now, hence the future upgrade.

I do like Steffen’s idea of adding a small secondary PV system, so I have some backup in place already. There may be room left on the workshop roof where all of this will be installed. To be researched.

And thanks for the compatibility warning concerning the three Multiplus units. I think I’ll break the budget for that one now, and install all three at once. That does trigger the max values I understood before for my battery, so I added a pre-charge kit in my drawing too.

A small suggested change:

Please remove the battery isolator switch. This type of switch gets hot even at low currents. I’ve already had to dismantle an installation because of this.

For pre-charging, check the NKON battery manual to see whether it has a soft start.

That battery is too weak for 3 MultiPlus 5000s.

For a grid-parallel ESS system, a MultiPlus 3000 or 5000 is often more than enough.

I’d also consider a Multi RS Solar. Unfortunately, it’s a rather niche product.

I’d also recommend a WiFi GX display.

Otherwise, have fun and good luck with the blue boxes!

A 16 kW battery for a three-phase system is perfectly fine; it’s a little above the minimum with 3 × MultiPlus 5000s (12 kW is the minimum; I have 20 kW myself).

The NKON’s BMS is rated for a maximum of 200 A. An MP5000 can manage that on its own for a few seconds. In my opinion, if you want to go off-grid, you should size the system accordingly. But yes, running in parallel with the grid probably won’t cause any problems.

The 16kW NKON batteries have a recommended discharge/charge current of only 150A

If I calculate (4000W/51.2V) × 1.15, I get around 90A

Plenty for one Multiplus 5000, too little for three

For the CAN bus, you need a terminating resistor at the Cerbo.
I can’t say whether the Type A cable will work, though.