I have 3 quattros currently wired for 3 phase output on AC out 1 and AC out 2. It is connected to a battery bank and solar inputs via the lynx distibution (and shunt and power in). The only AC input is a 3 phase generator on AC in 1. Is it possible to keep the 3 quattros for the 3-phase input but change the AC output to be split phase on just two of the quattros? Can I make AC out 1 split phase and AC out 2 three-phase? If either of those are possible, is there documentation?
If you have 3 120V quatros operating in a 3 phase setup, then the AC out’s are all120V L/N when on.
If you need a 240V split phase on one or more phases, then you will need an auto transformer for each phase that you want to generate split phase power, ending up with a 6 phase system (if all 3 phases are split). Auto transformers can be connected to either AC1 or AC2 outs.