TAB: General System frequency 50Hz Shore current 32.0 A Overruled by remote checked Dynamic current limiter unchecked External current sensor connected (see manual) unchecked State of charge when Bulk finished 85.0 % Battery capacity 132 Ah Charge efficiency 1.00 TAB: Grid Country / grid code standard Austria: TOR-Erzeuger A V1.1:2019-12 AC input 1 Above selected gridcode plus LOM B (compliant) TAB: TOR Erzeuger Typ A grid code settings Use Aux1 as disable FeedIn signal checked Maximum AC current for charge or feed in 100.0 % Maximum generated apparant power 100.0 % connect waiting time 60 s connect power ramp 0.0 seconds low frequency connect value 47.500 Hz high frequency connect value 50.100 Hz low voltage connect value 85.00 % Un high voltage connect value 109.00 % Un re-connect waiting time 300 s re-connect power ramp 600.0 seconds low frequency re-connect value 47.500 Hz high frequency re-connect value 50.100 Hz low voltage re-connect value 85.00 % Un high voltage re-connect value 109.00 % Un rise-in-voltage protection U> 111.00 % Un under voltage stage 1 80.00 % Un under voltage stage 1 delay 1.50 s over voltage stage 1 115.00 % Un over voltage stage 1 delay 0.00 s under frequency stage 1 47.500 Hz under frequency stage 1 delay 0.00 s over frequency stage 1 51.500 Hz over frequency stage 1 delay 0.00 s under voltage stage 2 77.75 % Un under voltage stage 2 delay 0.50 s over voltage stage 2 120.00 % Un over voltage stage 2 delay 0.00 s under frequency stage 2 47.000 Hz under frequency stage 2 delay 0.00 s over frequency stage 2 53.000 Hz over frequency stage 2 delay 0.00 s P(f>) start frequency 50.200 Hz P(f>) stop frequency 50.200 Hz P(f>) start delay 0.00 s P(f>) stop delay 30.00 s P(f>) droop 5.00 % P(f<) start frequency 45.000 Hz P(f<) stop frequency 45.000 Hz P(f<) start delay 0.00 s P(f<) stop delay 30.00 s P(f<) droop 5.00 % P(U) response Feed In reduced from Pnominal (= typ a) Volt-Watt curve voltage V1 90.00 % Un Max maximuminvert power at V1 100 % Volt-Watt curve voltage V2 95.00 % Un Max maximuminvert power at V2 100 % Volt-Watt curve voltage V3 110.00 % Un Max maximuminvert power at V2 100 % Volt-Watt curve voltage V4 112.00 % Un Max maximuminvert power at V4 0 % Filter time for P(U) 5.0 s Reactive power regulation Use a fixed Cos Phi Filter time for reactive power 5.0 s Cos phi at point 1 1.00 Use lock-in/out unchecked TAB: InverterPowerAssist unchecked Inverter output voltage 230 V Inverter DC shut-down voltage 37.20 V Inverter DC restart voltage 43.60 V Low DC alarm level 43.60 V Do not restart after short-circuit (VDE 2510-2 safety) unchecked enable AES checked Load for starting AES mode 69 W Offset for ending AES mode 46 W AES type search mode TAB: Charger Enable charger checked Weak AC input unchecked Stop after excessive bulk unchecked Lithium batteries unchecked Storage mode checked Use equalization (tubular plate traction battery curve) unchecked Charge curve Adaptive + BatterySafe Absorption voltage 57.60 V Float voltage 55.20 V Charge current 35 A Repeated absorption time 1.00 Hr Repeated absorption interval 7.00 Days Maximum absorption time 8 Hr Temperature compensation -64.8 mV/deg TAB: Virtual switchHTAB: Usage Virtual switch usage Do not use VS TAB: Assistants TAB: Assistant Configuration ESS (Energy Storage System) (size:1018) *) System uses Gel or AGM batteries *) The battery capacity of the system is 132 Ah. *) Sustain voltage during the first 24 hours of sustain 46.00 V. Sustain voltage after 24 hours 50.00 V. *) Cut off voltage for a discharge current of: 0.005 C= 48.00 V 0.25 C= 46.60 V 0.7 C= 45.60 V 2 C= 44.80 V *) Inverting is allowed again when voltage rises 1.20 V above cut-off(0). *) Relevant VEConfigure settings: - Battery capacity 132 Ah. - PowerAssist unchecked - Lithium batteries unchecked - Dynamic current limiter unchecked - Storage mode checked Total size of all assistants including the required (hidden) system assistants is: 1077