Graeme Duthie Solar System TAB: General System frequency 50Hz Shore current 50.0 A Overruled by remote checked Dynamic current limiter checked External current sensor connected (see manual) unchecked State of charge when Bulk finished 95.0 % Battery capacity 100 Ah Charge efficiency 0.98 TAB: Grid Country / grid code standard New Zealand: AS/NZS 4777.2:2015 (AC Neutral path not externally joined) LOM detection AC input 1 Type B (grid code compliant) TAB: AS/NZS 4777 grid code settings rise-in-voltage protection U> 248.0 V Power ramp time 360 seconds Enable DRM0 functionality unchecked Fstop for sustained high frequency operation 52.00 Hz Volt-Watt curve voltage V1 207.0 V Max charge power at V1 0 % Volt-Watt curve voltage V2 220.0 V Max charge power at V2 100 % Volt-Watt curve voltage V3 244.0 V Max charge power at V2 100 % Volt-Watt curve voltage V4 255.0 V Max invert power at V4 20 % Reactive power regulation Use a fixed Cos Phi Filter time for reactive power 3.3 s Cos phi at point 1 1.00 TAB: Inverter PowerAssist unchecked Inverter output voltage 230 V Inverter DC shut-down voltage 42.00 V Inverter DC restart voltage 44.80 V Low DC alarm level 44.80 V Do not restart after short-circuit (VDE 2510-2 safety) unchecked enable AES unchecked TAB: Charger Enable charger checked Weak AC input checked Stop after excessive bulk unchecked Lithium batteries checked Charge curve Fixed Absorption voltage 57.40 V Float voltage 57.39 V Charge current 70 A Repeated absorption time 1.00 Hr Repeated absorption interval 1.00 Days Absorption time 1 Hr TAB: Virtual switch TAB: Usage Virtual switch usage Do not use VS TAB: Assistants TAB: Assistant Configuration ESS (Energy Storage System) (size:953) *) System uses LiFePo4 with other type BMS (This can be either a BMS connected via CAN bus or a BMS system in which the batteries are protected from high/low cell voltages by external equipment.) *) The battery capacity of the system is 100 Ah. *) Sustain voltage 44.00 V. *) Cut off voltage for a discharge current of: 0.005 C= 46.00 V 0.25 C= 46.00 V 0.7 C= 46.00 V 2 C= 46.00 V *) Inverting is allowed again when voltage rises 1.20 V above cut-off(0). *) Relevant VEConfigure settings: - Battery capacity 100 Ah. - PowerAssist unchecked - Lithium batteries checked - Dynamic current limiter checked - Storage mode unchecked Total size of all assistants including the required (hidden) system assistants is: 1012