TAB: General System frequency 50Hz Shore current 25.0 A Overruled by remote checked Dynamic current limiter unchecked External current sensor connected (see manual) checked State of charge when Bulk finished 85.0 % Battery capacity 450 Ah Charge efficiency 1.00 TAB: Grid Country / grid code standard New Zealand: AS/NZS 4777.2:2015 (AC Neutral Path externally joined) LOM detection AC input 1 Type B (grid code compliant) TAB: AS/NZS 4777 grid code settings rise-in-voltage protection U> 258.0 V Power ramp time 360 seconds Enable DRM0 functionality unchecked Fstop for sustained high frequency operation 52.00 Hz Volt-Watt curve voltage V1 207.0 V Max charge power at V1 0 % Volt-Watt curve voltage V2 220.0 V Max charge power at V2 100 % Volt-Watt curve voltage V3 244.0 V Max charge power at V2 100 % Volt-Watt curve voltage V4 255.0 V Max invert power at V4 20 % Reactive power regulation Use a fixed Cos Phi Filter time for reactive power 3.3 s Cos phi at point 1 1.00 TAB: Inverter PowerAssist unchecked Inverter output voltage 230 V Inverter DC shut-down voltage 44.00 V Inverter DC restart voltage 48.00 V Low DC alarm level 48.00 V Do not restart after short-circuit (VDE 2510-2 safety) unchecked enable AES unchecked TAB: Charger Enable charger checked Weak AC input unchecked Stop after excessive bulk unchecked Lithium batteries checked Use equalization (tubular plate traction battery curve) unchecked Charge curve Fixed Absorption voltage 52.00 V Float voltage 51.00 V Charge current 70 A Repeated absorption time 0.50 Hr Repeated absorption interval 1.00 Days Absorption time 1 Hr TAB: Virtual switch TAB: Usage Virtual switch usage Do not use VS TAB: Assistants TAB: Assistant Configuration ESS (Energy Storage System) (size:1709) *) System uses LiFePo4 with other type BMS (This can be either a BMS connected via CAN bus or a BMS system in which the batteries are protected from high/low cell voltages by external equipment.) *) The battery capacity of the system is 450 Ah. *) Sustain voltage 48.00 V. *) Cut off voltage for a discharge current of: 0.005 C= 46.00 V 0.25 C= 46.00 V 0.7 C= 46.00 V 2 C= 46.00 V *) Inverting is allowed again when voltage rises 1.20 V above cut-off(0). *) The solar converter will start reducing its output power at 50.20 Hz. Output power will be reduced to minimum when the frequency is 52.70 Hz. The converter will disconnect when the frequency is higher than 53.00 Hz. *) Total installed PV inverter power is 5000 Watts. Total installed PV panel power is 5580 Watts. *) Relevant VEConfigure settings: - Battery capacity 450 Ah. - PowerAssist unchecked - Lithium batteries checked - Dynamic current limiter unchecked - Storage mode unchecked generator start and stop (size:184) *) Use primary programmable relay to start generator. *) Close relay to start generator. *) Start generator when the state of charge is lower than 35 %. *) Stop generator when state of charge is higher than 80 %. *) The generator is not stopped by AC input. Total size of all assistants including the required (hidden) system assistants is: 1973