question

mclgeneragl avatar image
mclgeneragl asked

SmartSolar Charge Controller MPPT 150/35 MPPT Error #28 Power stage issue Q2

Reference my previous question...

SmartSolar Charge Controller MPPT 150/35 MPPT Error #28 Power stage issue - Victron Community (victronenergy.com)

So I've sent my unit in for warranty, and the repair station is telling me I've overloaded it and caused the damage - Warranty Denied.

I suspect the unit was faulty from original manufacture, because I was never able to produce the power expected. Originally I had 8 solar panels and could only produce about 500 Watts. Here’s a typical screen shot under full sun…

8-panel-configuration.png

Since I was never producing more than about 500 watts with my bank of 8 panels, I decided to go up to 16 panels. The spec sheet says that if more power is connected, the controller will limit input power. I made sure I didn’t exceed the 150V and 40 amp input maximums. VOC is only 109.6V with 4 panels in series, and ISC is only 35.92 with 4 panels in parallel. Shouldn’t the MPPT be able to handle this setup?

mppt-150-35-spec-sheet.png

solar-panel-spec-sheet.jpg


MPPT Controllerserror
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
wkirby avatar image
wkirby answered ·

I can't really see how you could have "overloaded" it. Further, how could they tell?
You can only go over the Voltage limit - which you have not according to the PV module specifications.
It's unlikely that Isc could have been exceeded even with cloud edge. I suspect if this did happen that there would be more of a catastrophic failure and some of the smoke would have come out.

The description for error 28 says that the unit should be replaced, simple solution. I think your repair station should simply process the warranty and get you back in business.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mclgeneragl avatar image mclgeneragl commented ·
Thanks @WKirby, I really want to get the system working again, but I’m hesitant to buy Victron again if they don’t honour their warranty.
0 Likes 0 ·
Paul B avatar image Paul B mclgeneragl commented ·
I Agree with Wkirby, I am Sure that Victron would replace the unit without issue.
0 Likes 0 ·
mclgeneragl avatar image
mclgeneragl answered ·

I pressed the issue with the repair station. They submitted the unit to Victron for warranty consideration and the unit was replaced under warranty. I bought a second unit and will now run only 1600 Watts on each. Thanks for your help on this @WKirby and @Paul B.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

MPPT Product Page

MPPT Error codes

MPPT 150/60 up to 250/70 Manual

Additional resources still need to be added for this topic