How to cut off current generated by inverters in mode 3

Hi everybody,


We are considering the possibility of installing 3 units of Multiplus II 48/3000/35-32 with one battery in a tertiary building in Spain.

The idea woud be that these 3 Multiplus II, would act as reversible chargers / inverters working in mode 3 and, thus, following the power setpoints established by an external control loop through Modbus TCP. This is for R&D purposes and we only want to make a pilot proving that it is feasible to store electrical energy during night (low kWh price) and use it inside the building during day (high kWh price). Economical profitability is not the focus in this pilot.

AC-IN terminals of the Multiplus II units would be connected to the bars of the main switchboard in the building by means of a 4-pole contactor (among other switchgear). See diagram:


AC-OUT terminals will be idle, that is, although you can see some wiring and switchgear in the diagram to enable future connection of critical loads, this only would happen prior to reconfiguration of ESS to mode 1 (Keep batteries charged) for the multis to act as a UPS. Again, for the purpose of my question, no critical loads will be connected, AC-OUT terminals will be idle, and configuration will be in mode 3 (external control).

Contactor -K1 in the diagram will be governed by an INDEPENDENT system which will monitor energy going through a grid meter and will open the contactor whenever the power generated by inverters is being fed back to the public grid.

The thing is that I don't know how to size contactor -K1 in the diagram. I can see that sizing should take into account two cases:

a) When charging battery, I can assume that current will not exceed 32 A in any case, according to the Multiplus II datasheet.

b) When inverting, I assume that the maximum current through the contactor will be 3000VA/230V= 13 A. But my concern is that here the inverters are working as a CURRENT SOURCE rather that as a voltage source because they are following the Modbus TCP power setpoint.

Therefore, my questions are:

1. Could it be the case that the inverters "push harder" when they see contactor's opening? Would it be enough to put a contactor with rated current of 32 A (Utilization catetory AC-1) to account for case (a) or should I put a contactor with higher rated current (or harder utilization category) to account for case (b)?

2. How long will it take for inverters to realize that they cannot fulfill the power setpoint in the Modbus TCP map and stop trying?

3. Can this situation be harmful for the inverters?

4. In the end, which will be the error status of inverters? Will I be able to rearm them through Modbus TCP or only on-site?


Thank you very much in advance (and sorry for the length of the question).

Multiplus-IIModbus TCP
1551107478564.png (348.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
boekel avatar image
boekel answered ·

32A contactors should be plenty.


But why Mode 3 vs Mode 2? or Mode 1?

basically you want the system to charge at a certain time (scheduled charging)
And supply the loads during high tariff time (normal Mode 1 behavior)

of course you need a power meter in the grid connection for the Victron system to know if it has to send power to the system.

another option is to use Mode 2 and set a 'charge' setpoint during low tariff hours, and a 50-200W grid setpoint (to prevent accidental feed-in) during high tariff hours.

(sorry I don't have the knowledge to help you with the other questions)

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

angel avatar image
angel answered ·

Yes, I know it sounds strange. It is and R&D project. Electrical storage is one asset but there are other assets (e.g. HVAC system) and the overall algorithm must be in control of every asset (without intelligence in the asset itself). Therefore mode 3 and control through Modbus TCP is a prerequisite.


And my focus is on what happens if an external safety system (zero-feed back) decides to open the contactor.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image boekel ♦ commented ·

Cool project, I hope you can share some of the things you learn?

I'd guess the inverters will power down due to a high voltage error when you open the relay and ask for more power than the users can take, but again: I'm no expert in this so I hope someone else can answer this for you.

0 Likes 0 ·