Multiplus stopped working after SOC reset on BMV 700

The Multiplus 24/3000 immediately stopped working after I had synced the SOC on the BMV-700 by pressing the "+ -" keys in normal operation. Since then it does not do anything anymore.

A hint to solve this problem would be highly appreciated.

Thank you!

Multiplus-IISOC
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·
Measuring your battery voltage would be the very first step.
0 Likes 0 ·
3 Answers
georgeleonardo avatar image
georgeleonardo answered ·

Having a very similar issue. Does your Multiplus turn any lights on?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

chris-wy avatar image
chris-wy answered ·

Battery voltage is ok as measured at the inverter's terminals.

No light turns on.

Tomorrow I might know more I hope.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

chris-wy avatar image
chris-wy answered ·

solved: most probably the remote switch cable went loose inside the display's box.