Quattro 10K 120V - No AC Load connected / Generator on / deep unbalance L1 vs L2 which charging the battery

The system is configured with two 10K Quattros 120V/240V Split phase with 4 SmartSolar Charge controllers, a Lithium Battery with a CAN-bus BMS and it also has a Lynx Ion Shunt. ESS is the only assistant configured in the Venus GX.

I am having a problem of unbalance L1 / L2 in ACin1(Generator). When there is no AC load connected, Grid is off, Generator is on, and battery is at 49% SOC the Quattros use correctly the generator to charge the battery, but it creates an unbalance situation, where L1 goes up to 3000W and L2 stays at 10W. This states is held for a few minutes until the Quattro give up and disconnects the ACin1(Generator) and stops charging.

So the only load in the system is the battery, for that the Quattro's need to rectify the electricity from the Generator, but it does it in an unbalance way. How can I tell the Quattros to pull the same or similar amount of power from L1 and L2 of the generator?

Thanks

battery chargingGeneratorVenus GX - VGX
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

natebert avatar image natebert commented ·

Is your generator 120v or 240v?

Is your inverter arrangement trying to create 120v/240v splitphase?

0 Likes 0 ·
Carlo avatar image Carlo natebert commented ·

Yes it is!

0 Likes 0 ·
2 Answers
boekel avatar image
boekel answered ·

did you measure the L1/L2 voltages when this happens? maybe the voltages are not stable?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Carlo avatar image
Carlo answered ·

Yes the L1 and L2 voltage was stable at 120 to 122V.

Frequency was at 60.3Hz



1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image boekel ♦ commented ·

ok, and what settings do you use for LOM detection?


(also posted to other thread, might be better to continue this question here)

0 Likes 0 ·

Related Resources

Additional resources still need to be added for this topic

MultiPlus Generator FAQ

GX - Generator auto start/stop

Automatic Generator start/stop

 Hybrid Generators

Virtual switch - Generator start/stop

Venus GX manual

Venus GX product page

Additional resources still need to be added for this topic