How efficient is my Victron 12/500 inverter?

Does anyone have a link to a graph or something? :-)
Thanks!

MPPT ControllersPhoenix Inverter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
Alexandra avatar image
Alexandra answered ·

@Mathew Hamilton Green

I have found it depends on your load and set up. So it is a difficult one to answer in a datasheet as there are so many variables. Even percentage load of inverter capacity is a factor.

The best way to know how efficient your personal setup is, is to run a known load on your system, and measure how much is being drawn from your battery and work out the percentage from there.

For example

I have a 24/3000 and am running my heating element of 1500W yest i am drawing 1600 watts from the battery I know I have about a 93% efficiency for that circuit and load. Of course I have a low frequency Multiplus inverter not a high frequency like the newer ones, this is also a factor to consider. Recently increased the battery cable size from 50mm to 95mm ad made the system more efficient that way.

I have used a simple element as an example of a load as it has a good power factor. Some led bulbs have a power factor of 0.5 so a 4w bulb can actually draw 8w from a system. So checking with a clamp meter on incoming and outgoing is helpful to see what side the inefficiency is.

16 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

@Alexandra

Hi,

Are those numbers for real, or just mathematical an example?

My MP-II 48/3000 paints quite different picture.

Same type load (heating element) but efficiency is much lower.

Very disappointing 84.4%. :(

Regards,

Marek


inv-eff.jpg

0 Likes 0 ·
inv-eff.jpg (71.9 KiB)
Alexandra avatar image Alexandra ♦ marekp commented ·

W

@MarekP

No we used the color control as well. But checked numbers with a clamp meter.

Found interesting changes when

  1. Battery type was changed is from lithium to agm. Battery efficiency is a factor.
  2. Cable size changes as well we use 95mm now (makes sense as there will be less resistance). And the usual removal of extra things in the wiring and left just fusing and the bmv shunt. Good lug crimping also makes a difference. All resistance connections are important.
  3. The other thing that made a difference was measuring with the bmv shunt as the multi itself has no way to actually measure power from the battery. So the figure coming out is usually an assumed amount.
  4. Wiring on the ac output was also 'tuned up'

Thats why we say efficiency to some degree can be affected by setup.

We have a 24/3000 which is technically less efficient conversion wise.

0 Likes 0 ·
marekp avatar image marekp Alexandra ♦ commented ·

@Alexandra

Hi,

I understand all your points but, as you can see in my picture, the numbers are from MP-II unit itself.

It calculates incoming/outgoing power from battery/AC by measuring the current and voltage on its battery and AC terminals.

Cables, fuses shunts are out of this equation.


Regards,

Marek

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ marekp commented ·

@MarekP

Since voltage drop under load is an issue for most batteries the figures showing power out are not a measured thing only an assumed thing.

Cables fuses and shunts add resistance that makes voltage drop between the battery and the multi. So what the multi measures is not necessarily what is being drawn from the battery.

That's why shunts for bmv are placed near the battery.

0 Likes 0 ·
marekp avatar image marekp Alexandra ♦ commented ·

@Alexandra

Hi,

MP-II measures "V" and "I" at its terminals and has no clue what happens on the cables outside its box.

It does not care about the battery's voltage drop.

It measures voltage and current than calculates the power provided on the battery terminals and taken on the AC-out terminals.

Imagine yourself in the room with voltmeter, current meter and calculator.

With those you are measuring voltage and current in the junction box on the wall and calculate the power.

You do not know or care about the voltage in the power-plant 100km away or electrical oven next room.

Knowing power IN and power OUT you can calculate the efficiency of equipment in the room.

This room is the MP-II. :)

What I am trying to say is that I am not looking/asking for the efficiency of the whole system, from battery to refrigerator.

I am asking for the efficiency of the MP-II only.

Regards,

Marek


0 Likes 0 ·
marekp avatar image marekp Alexandra ♦ commented ·

@Alexandra

Hi,

I know the official specification of MP-II.

I says that efficiency is MAX 95%.

When you wrote that your MP-II 24/3000 has 93% efficiency, I asked you if you measured it.

Your answer was not very specific.

You started adding other elements of the system and suggested that they influence the efficiency of the MP-II itself.

I agree, they do have an input on the efficiency of the whole system but have no input on the efficiency of the MP-II itself.

If you saying that your whole system has the efficiency of 93%, than I do not believe you.

In the last link you posted I found this table.

screen-shot-2021-01-13-at-113402-pm.png

My MP-II was loaded with 1100W (for maybe 5 minutes) and efficiency of inverting was at best 88%. It is far from 93% with your 1500kW load.

screen-shot-2020-11-27-at-11522-am.png

screen-shot-2020-11-27-at-11522-am.png

Can I ask for warranty repair on my MP-II for low efficiency.

Regards,

Marek

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ marekp commented ·

@MarekP

Measured with our own test equipment and meters. The several different set up used are too detailed to post here since this is someone else question and thread and we did it for our own interests.

We then confirmed with what we see on the color control in the system.

Most systems have a whole system efficiency of about 88% (and lower) this includes other inverter makes and models in the same wiring set used on the Victron. This includes some inverters that claim 100% efficiency. (By the way just impossible).

So in the whole your system is ok, is it not doing something you want it to do?

93% is only achievable in the model circumstances. That is also including a temperature controlled environment. Real world application is usually far from such and so most likely most systems will never reach the same level, unless a ridiculous amount of time and money is spent to make it so.

We could continue debating this for ever on so many different points but the truth of the matter only someone on the ground by your system would be able to really help you.

Have you read this paper?

https://www.victronenergy.com/upload/documents/Output-rating-operating-temperature-and-efficiency.pdf

0 Likes 0 ·
marekp avatar image marekp Alexandra ♦ commented ·

@Alexandra

Hi,

I do not know why my point is not getting trough to you.

It is probably fact that English is my second language.

I will try again.

In the beginning of this system we have Sun for PV or gasoline for GEN.

At the end we have our equipment running on the electricity.

Somewhere in between we have battery and Victron stuff.

Each component of this system has its own efficiency, wires, fuses, shunts included.

Total efficiency of the system is a product (math) of all individual efficiencies. A*B*C*...X=RESULTING EFF.

MP-II is a one item in this chain with its own efficiency.

I am asking about this individual efficiency of the MP-II.

Specification quotes that it is max 95%.

When you go to the store and buy an inverter (ea. 48VDC to 230VAC), the seller tells you that it has ea. 90% efficiency. This efficiency does not include the efficiency of the battery or DC wires.

So in the whole your system is ok, is it not doing something you want it to do?

My system works but efficiency of the MP-II is disappointing.

With this low efficiency the idea of this system is not achieved.

The idea was to build the system with 24 hour efficiency better than 80%.

In my country I can store my PV energy in the grid with 80% efficiency and ZERO cost of investment in such a storage place.

Idea was to store my PV energy in the batteries for later when Sun is not shining (night).

I could do it by storing this energy in the grid with 80% efficiency.

I wanted to better that by storing energy in the battery that has over 95% efficiency and "invert" it with MP-II at 95% efficiency.

Resulting efficiency would be over 90%.

But when MP-II has "real life" efficiency lover than 85% the whole idea is DOA.

We could continue debating this for ever on so many different points but the truth of the matter only someone on the ground by your system would
 be able to really help you.

Again my problem is with the efficiency of the MP-II being so low.

The rest of the system is OK.

Have you read this paper?
https://www.victronenergy.com/upload/documents/Output-rating-operating-temperature-and-efficiency.pdf 

From where, you think, I got the table with efficiencies?

Regards,

Marek

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ marekp commented ·

I did understand your point.

My point is in real life circumstances your system is what is usually as in the average installation. Even compared to other brands installed in the same situation in the same wiring set and conditions.

Is Victron is not worse than other products in this regard? In my experience no.

0 Likes 0 ·
marekp avatar image marekp Alexandra ♦ commented ·

@Alexandra

Hi,

Is Victron worse than other products in this regard? In my experience no.

It is worse than it's specification claims it to be, and this is now my problem.

Regards,

Marek

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ marekp commented ·

@MarekP

And do other inverters have the same issues. Yes. They are all have the same efficiency problems. All inverters have efficiency curves.

What we try and do is size the system to work an inverter at it's best efficiency point. So if your base load is 800w you size an inverter that works best and most efficient at that load.

The thing with victron is their monitoring is such that you can see exactly what the system now doing. And so deficiencies in setup and other issues become more apparent. If they didn't you would be blissfully unaware as most inverter users are with less monitoring and therefore quite happy you had reliable power.

0 Likes 0 ·
Show more comments
Alexandra avatar image
Alexandra answered ·

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mathew Hamilton Green avatar image
Mathew Hamilton Green answered ·

Nice thanks! :-)

I have two 120Ah batteries in parallel and my Mac Mini M1 and monitor is drawing around 4Amps, when in use and my LED smart light around half an amp... I am trying to see how long I can go between charges because in theory I should get around 24 hours of operation. I also wanted to check the batteries as I have had them just over a year and wanted to see how they were doing! :-)

Just wanted to check everything.

I'm about to install another 270W solar panel to bring my total to 810W as I am determined to be able to power all my needs from the sun even in the winter in England. Today I was drawing around 3Ah all day... I am in a motorhome not in situ somewhere! :-)

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

@Mathew Hamilton Green

Hi,

If I understand your question correctly, you have 2x12v batteries 120Ah each.

That gives you 2880Wh of energy when they are fully charged.

If they are of Pb type, you can only use half of it if you want them to last the reasonable time.

Your load is 4A at 230V that makes it 920W per hour

If we assume that your inverter has 100% efficiency and 50% use of battery, you have around 1h and 33 minutes of battery power when there is no Sun to charge your battery.

Regards,

Marek

0 Likes 0 ·
ripper avatar image
ripper answered ·

https://www.photovoltaikforum.com/thread/133886-effizienzkurven-wechselrichter-victron-oder-fahre-ich-mit-2-wechselrichtern-wirk/


Here is a Graph of a 375 vs an old 3000 I measured. It is always a curve. Sweet spot is around half of nominal load which will be similar on your 500 unit. I am running 2 Inverters, above 200ish W load the little 375 uses more battery power than the big 3000 inverter. If you are off grid no load consumption is the more interesting value. 4W or 0.5W (eco mode) for the little one vs 12W for the 3000 vs 25W cheap chinese product 24/7

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.