High voltage alarm when voltage looks ok

img-20201222-182418.jpgBMV has been triggering high voltage alarm over the last 24 HRS yet I see battery voltage to be normalimg-20201223-072921.jpg

battery system voltage
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

The high voltage alarm clear value is set to 1V, this is the voltage that the battery needs to get to clear the alarm.

Tap the High voltage alarm, and set the Clear Value to 28.4V

Then when the battery voltage falls below that value, the alarm will stop.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jairus Onsafari avatar image Jairus Onsafari commented ·

Thanks Guy, it worked. Alarm clear value was very low. Bravo.

0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ Jairus Onsafari commented ·

Success!

0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi @Jairus Onsafari,

Check the BMV settings in VictronConnect, in the Misc menu, to make sure that the Aux input setting is correct. For example if you have the battery mid-point selected, but wired across the full bank (instead of the midpoint of the battery) you will get an alarm.

Then check the alarm settings and make sure the alarm thresholds are correct.

Maybe post some more screenshots of those settings screens if that doesn't help.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Jairus Onsafari avatar image Jairus Onsafari commented ·

BMV Misc settings are as in picimg-20201223-082733.jpg

0 Likes 0 ·
Jairus Onsafari avatar image Jairus Onsafari commented ·

And here are my alarm settingsimg-20201223-084235.jpg

0 Likes 0 ·