L3 overload with practically no load.

Hello,

I have 3-phase system build on EasySolar-II GX (phase L1), 2x Multiplus-II (phase L2 and L3)

There is no ESS assistant loaded only Two-signai BMS.

First time this system reported overload on phase L3 twice.

It happened when there was grid loss for less than a minute.

System is under development and there is practically no load (50-60W)

Why this overload happen?

log.jpg

advanced.jpg

Multiplus-IIEasySolar All-in-One3 phase
log.jpg (40.3 KiB)
advanced.jpg (85.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Warwick Bruce Chapman avatar image
Warwick Bruce Chapman answered ·

This may be related to an ongoing issue that is being investigated. What is the quality of grid?

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

My system is connected to this grid for the last 6 months.

Grid is not perfect and this is why I invested allot of money for this Victron hardware and battery, but this overload happened first time since the instalation of the system.


0 Likes 0 ·
Warwick Bruce Chapman avatar image Warwick Bruce Chapman marekp commented ·

Any chance you recently updated firmware? What version you on?

0 Likes 0 ·
marekp avatar image marekp Warwick Bruce Chapman commented ·

No, I did not update the firmware recently.

I do not remember what it is but it was updated to the latest at the time of first install.

EDIT.

Firmware is 475

0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @MarekP

I see the overload -warning- happens when the grid fails, this can happen when the grid voltage drops 'slowly' and the system has to bring back the voltage to normal system voltage.

An overload -warning- doesn't have to be a problem, an -alarm- is a problem.

What are you grid low voltage disconnect values?

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·

@Daniël Boekel (Victron Energy Staff)

Hi,

When those overload warnings happened the voltage changes were fast.

Linesmen just tripped the breaker, to perform some work on the grid.

Puzzles me that this overload warning happened, with 0W load on all three phases, and only on phase L3.

screen-shot-2020-11-24-at-94125-pm.png

You have seen my grid voltage disconnect values. :)

But here they are:

2.jpg

What is also interesting that they were not some short blips. One lasted 75 sec and the other 48 sec.

Regards,

Marek

0 Likes 0 ·
marekp avatar image marekp marekp commented ·
0 Likes 0 ·
Daniël Boekel (Victron Energy Staff) avatar image Daniël Boekel (Victron Energy Staff) ♦♦ marekp commented ·

@MarekP

I'm sorry but I don't see the issue...a -warning- is not a problem, an -alarm- is.

0 Likes 0 ·
marekp avatar image marekp Daniël Boekel (Victron Energy Staff) ♦♦ commented ·

@Daniël Boekel (Victron Energy Staff)

Than why this warning is even reported, when you telling me to ignore it?

screen-shot-2020-11-30-at-10310-pm.png

You want me to ignore it and wait the problem?

0 Likes 0 ·
marekp avatar image
marekp answered ·

@Daniël Boekel (Victron Energy Staff)

@Guy Stewart (Victron Community Manager)

I really would like to know the answer to my question.

I cannot agree with the answer that tells me that I should ignore this overload warning only because it is not an alarm.

If warnings are unimportant than why you even bother to program them to the system?

If it is a bug than you should fix it.

It is without logic to have an overload warning w ZERO load.