Voltage Sense Wires using 2 Multiplus Inverters

I installed Voltage sense wires to my battery bank on the L2 or slave inverter and it does not seem to be seeing the difference in voltage that the batteries are at when under load. It still appear to be getting its info from the inverter cables. Do I need to enable this somewhere or does it need to be connected to the master inverter?

battery system voltage
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems#communication_wiring

"Wire the voltage sense on the master of L1.
(If the system has more than 1 AC input, connect it to the Master corresponding to the first AC input.)"