markarivard avatar image
Can I use a Victron Multiplus Inverter Charger 2000 W 12 V on an RV with 50 AMP Shore power?
I have a 2018 Montana 5th Wheel with 50 AMP shore power and no inverter at this time. My goal is to install an inverter, 2 - 100 ah Battle Born batteries, 712 Battery monitor, and portable generator now. Future will add ground and roof Solar with additional batteries.
Questions:
Can I use a Multiplus Inv/Charger 2000w on a 50 AMP service as described above?
Is there a wiring diagram out there to help me get this set up?
I assume I will only run one of the hot lines from the 50 AMP through the inverter.
MultiPlus Quattro Inverter Chargeramps
Kevin Windrem avatar image
Kevin Windrem answered ·
I have a 2000 watt Multi and 200 AH Battleborns like you are planning but with a 30-amp service. The multi is between shore inlet and the AC distribution. Works extremely well but you do need to manage loads manually when on inverter.
The best solution would of course add a second inverter for the other leg and at least one more battery. Running two 2000 watt inverters on 200 AH @ 12 volt of batteries would be very marginal.
sglad's solution seems like a good one and covers most of the bases if a second inverter and more batteries isn't in the budget.
A manual switch in the L2 input to the AC distribution panel would do much the same thing but you'd need to move the switch when using shore vs inverter power.
Your original plan to put the Multi on one leg of your shore power is certainly less cost but has the drawback of needing to arrange RV loads to be on the "inverter" side of the AC distribution panel.
There are also manually operated manual transfer switches designed for home standby generators that could allow more flexibility, switching up to 12 circuits between the main AC distribution circuit and the inverter (using the transfer switch's generator input).
I'd highly recommend air conditioner soft start devices like the MicroAir. They make running an AC on a small inverter or small generator possible.
sglad avatar image
sglad answered ·
Victron's 2000 watt inverter is 1600 continuous so it might not run run your microwave. Best to get 3000 watt which is 2400 continuous and will run a 1800 watt microwave.
You don't connect one leg of 50 amp service directly to inverter. You will need a subpanel or something like AM Solar's SMS https://amsolar.com/rv-inverter-accessories/50-tsfmb1
200 ah of batteries is on the low side but doable.
crazy-marty avatar image
crazy-marty answered ·
I use a 3000 Watt inverter on 3 Battleborn's Mine has a built in transfer switch and is built for 50 amp service.
You mush have a transfer switch in the system so you do not burn things up. This will allow shore power to flow through it and not run the inverter.