BMV-700 "Current"/"Power" read-outs don't change to positive when connected to RV solar panels

My BMV-700 indicates increased "battery voltage" when connected to AC house current (charging), and when connected to my RV solar cells (2 110 watt). When connected to AC, the "Current" and "Power" readings go from negative to a positive reading, but don't change when connected to my solar cells. Why not?

solar
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

I guess the negative of the PV charge controller is connected directly to the battery instead to the"load" side of the BMV shunt.