ET340, Multiplus II GX and external non critical loads

Good day Victron Community,


Using an ET340 and a Multiplus II GX I have gathered that a Single phase Inverter would have to be installed on L1.

I would like to know if the GX is capable of Calculating correctly and Controlling the following System

The specific Question is whether the GX will be able to calculate that there are external loads between the ET340 and its AC Input?

I am attempting this approach to avoid the limitation of 32A Maximum Non-Essential loads and having to route these through AC-Out 2. I also want the added benefit of measuring and logging L2 and L3 Non Essential Loads.


Kind Regards

Randolf Wenhold


Multiplus-IIEnergy Metergx
1571387965686.png (22.1 KiB)
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Murray van Graan avatar image

Hi Randolf, that is correct. The ET340 and GX device will be able to see the ac loads between energy meter and multi input. Further it will also accurately measure and log the consumption on the other two phases, and those you will be able to view on VRM. I have quite a few of these systems installed and running correctly (single phase multi on L1 with an ET340 monitoring all three phases)

2 comments Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

I was wondering where "Murraynated" went and I couldn't fathom how I hadn't seen these answers before and yet they sounded so familiar... Welcome Murray van Graan!