question

luis avatar image
luis asked

Generator not detected by CCGX

I have an off-grid system two Quattros 48/15000 with PV inverter in AC-Out 1 and two BYD 10 kWh batteries.

I have wired the generator in AC-In 1 of the Quattros and set "Generator" in AC-In 1 and nothing in AC-In 2. I have AC-In power to start the Quattros but CCGX is not detecting main power in AC-In.

AC-Out 1 power is delivered by the batteries which are permanently been discharged and not been charged.


CCGX Color ControlGeneratoroffgrid
1570612606759.png (19.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
stevo07 avatar image
stevo07 answered ยท

What generator are you using? Have you tried enabling the 'weak AC' within VE Config?


Why is your battery voltage showing 11.4V if using BYD?

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

luis avatar image luis commented ยท

There is a problem (COM, firmware, whatever...) with the BYD batteries. This morning the batteries were discharging and feeding into the microgrid and then Generator started to deliver.

Generator is 14 kVA, powerful enough, so I didn't enable weak AC

0 Likes 0 ยท
Show more comments