logoszm avatar image
logoszm asked
Is AC2 load limited to inverter capacity
It is my understanding that AC2 can be utilised for non-essential loads and given that surplus PV output is available, the surplus can feed these non-essential loads when grid supply is present. My question is if there is a limit on the current through AC2? Could I, for example, connect a potential 20A load on AC2, such a water heater in addition to a 15A essential load on AC1?
ac out 2
Kevin Windrem avatar image
Kevin Windrem answered ·
Victron specifies a maximum current on the AC 2 output. Check the spec sheet for your particular model. It is not tied to inverter capacity.
AC input power also has a limit and this would be shared between the AC 1 and AC 2 outputs.
Power assist is added to the shared output power (AC input plus inverter capacity).
PV inverters connected to the output of the Multi/Quattro would be available as additional power as well. PV inverters connected to the INPUT of the Multi/Quattro would only be available when grid power is present and would flow through the same input relay. It would therefore not increase the available power over the limits specified in the spec sheet.