Off grid system, nice big bank of batteries powered with a 6kW wind turbine and backup generator.

We've had a new lot of kit installed which is run by a Victron Quattro inverter/charger and colour control.

Our old system (Outback inverters) worked by feeding the power into our bank of batteries and then, when there was excess wind power, dumping that power to storage heaters which were hard wired into the system. It worked well. Power would only be dumped to heat when the house's needs were all met and the batteries were fully charged.

The new system dumps power whenever wind speeds are high which sounds ok, but in practice it's not working well for us. We've had several low-wind days and our batteries are therefore low, and now the wind speeds are picking up: so power is being dumped even though our batteries are still on a relatively low charge (last time I looked we were at about 58% according to the colour control) and with the washing machine running (nothing else) the level of charge in the batteries was actually dropping, despite the wind turbine belting round, because so much power is being dumped.

The batteries rarely get above 80% charge, and are frequently below 50%. We live in an area with very good wind speeds and relatively little turbulence, so the turbine is very efficient for us. Or at least, it was, before we had this new kit installed.

In addition we've realised that whenever our diesel generator is put on (the remote start no longer works since the new installation--we'll get round to that later) all the dump loads come on. We're paying for the generator to run, in order to dump 6kW of heat we do not need before our batteries are charged.

We've queried this all with our installer and he says the new system is working as it should. I am not convinced. I do not want to pay to run a generator to produce mostly heat--I don't want to dump any power when the generator is making it, because I want to minimise the hours the diesel generator runs. And I want to be able to run the washing machine, tumble dryer, and a few other things too, especially on high-wind days, but the dump loads mean I don't have the power to do that.

This can't be right, surely.

Advice?



offgrid
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

6 Answers
Chris avatar image
Chris answered ·

I feel your pain - and the devil is in the detail (and assistants! - often)

What is managing switching on the dump loads?


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

desperatedan avatar image
desperatedan answered ·

Installer says it's all controlled by the Quattro, and that the dump loads respond to increasing frequency as the wind speeds pick up. I am losing confidence in him, though, as he's now contradicted himself several times about how this all works.

With our previous system we could change everything using the control panel, but the Colour Control doesn't give us many options.



2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Chris avatar image
Chris answered ·

ahh yep - suspected this might be the case.

Generators often have a higher off load / low load frequency - up to 53hz or more. And also be unstable!

Also assuming they have configured the "PV inverter" assistant on the quattro .There are frequency thresholds that can be changed. It all has to match up and be carefully choreographed.

The quattro starts to ramp the grid frequency as the battery "approaches" being fully charged. This could be causing the dump loads to come in too early - if their frequency controlled switches are set too low. (unfortunately ive never been able to find any actual documentation for the %'s and what is meant exactly by "approaching" and have recently seen on a lithium battery system that it only happens actually at 100% SOC and not before)

Turbine output and quattro charge capacity is critical for avoiding over volt issues on the AC. But you may already be aware of that... just throwing it in there....

Its also best having the Colour Controllers internal relay managing the generator (it may or may not be?) As it has far more functionality (just a dump volt free relay for "run / dont run" control though)

10 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

desperatedan avatar image desperatedan commented ·

So with this system there’s no way to avoid dumping power when the generator’s running? If that’s true (and I don’t doubt you) then the system is not fit for purpose.

We don’t have PV, just a wind turbine—does that matter with regard to the “PV inverter assistant” you refer to?

You suggest that we should be able to change the point at which the frequencies change, and therefore the points at which the dump loads kick in, but we can’t find a way to do this using the Colour Control, which is how our installer told us we should change settings.

The generator’s remote start isn’t functioning. It hasn’t since the new kit was installed, so we can’t use the Colour Control to manage the generator at the moment. We’re trying to find out what the installers changed on the gen set to see if we can change it back, but they’re just insisting it’s all working fine and that we need to “get used to the new system”. Which isn’t very helpful.

This new system has resulted in us having less usable power, having to run our generator a whole lot more than we used to, and in our having to mess around with plug-in dump loads instead of them being hard-wired things we could forget about. It’s a disaster, and right now I cannot recommend Victron products—not to anyone who lives off-grid, as we do. From what I’ve now learned, here and elsewhere, it’s a major step backwards for us, compared to the set up we had before. And there’s little we can do about it, as the installer persuaded us to have our wind turbine rewired to a different set up which our old kit won’t work with. So we can’t revert to our previous set up. It’s such a mess.



0 Likes 0 ·
desperatedan avatar image desperatedan desperatedan commented ·

Is there a different way to control the dump loads? Because if there is, that might well sort out our problems.

0 Likes 0 ·
boekel avatar image boekel ♦ desperatedan commented ·

Hi @DesperateDan
I feel for you, but we have almost no information to help you.

I hope you've got a diagram of the installation so we can understand how things work?

0 Likes 0 ·
desperatedan avatar image desperatedan boekel ♦ commented ·

No, I don't have one. What information do you need? My problem lies solely with how dump loads are controlled when using the Quattro inverter-charger: I would assume they're relatively standard.

0 Likes 0 ·
boekel avatar image boekel ♦ desperatedan commented ·

Well at least the brand and type of the dump-load, as a start. No they're not all the same ;)

your installer should have provided a diagram with the system, so when he or her is not available someone else can help you...

0 Likes 0 ·
desperatedan avatar image desperatedan boekel ♦ commented ·
Our original dump loads are storage heaters. I don't remember the brand but I'm not sure why that would be helpful to you. We now can't use them as they are hard-wired into the wall and our installer has now given us devices to plug our dump loads into--lengths of cable with a plug at one end, a socket at the other, and a box of electronics in the middle. These apparently react to the increasing frequency of our incoming power and switch on at specified levels. I can't give you a brand because they don't have one on them--they look home-made to me, to be honest, and ugly as well.


Our installer should have given us a diagram, but he also should have left us with a system that works to our requirements, and he hasn't done that either. I am discovering more things every day that he either didn't do that he should have, or that he did wrong. It's a huge worry.

0 Likes 0 ·
boekel avatar image boekel ♦ desperatedan commented ·

Hi @DesperateDan, sorry to hear, maybe you can find another installer to check things?

There are multiple ways to switch dump loads, frequency shifting is one of them, and the Quattro is very capable of doing this (and if all settings are correct it does so only when battery is fully charged).

I'd first make sure everything is safely installed (does the brake function for the wind turbine still work with the controller changed?), a diagram can be made with this inspection.
If fundamentally sound, then it might just be changing some settings to get things right.


Wind turbine 6kW: is that the maximum power? and what size Quattro do you have?

0 Likes 0 ·
desperatedan avatar image desperatedan boekel ♦ commented ·

The wind turbine's brake is a handle at the base of the tower, so I doubt the inverter will affect it!

The wind turbine is rated at 6kW, so that's meant to be its maximum output but we've had more out of it in high winds.

Our Quattro has these numbers written on it: 48 (which is the voltage, isn't it?), 10000, then 140. So I assume it's the 10000VA model.

Is there a way to switch dump loads without using frequency shifting? Using the Quattro inverter/charger? Because it's just not working for us--high winds again today, very little load on, and the battery charge percentage is dropping once again because all the dump loads are burning through our power. The charge got so low yesterday, despite the high winds, that we unplugged the dump loads and allowed the charge to rise before plugging them in again overnight--and here we are again with low battery charge despite the high winds. It's just so disheartening, and whenever we ask the installer about it he insists the system is working as it should.

0 Likes 0 ·
sean avatar image sean desperatedan commented ·

Could you provide a list of all of the equipment that's been installed please - specifically anything likely to be sat between the WT and the inverter (excluding any protection devices).

Perhaps then we can then figure if your system could be configured to function as per your expectation.

Is the WT a Proven/Kingspan/Evance/Elotec or something less durable ?

0 Likes 0 ·
sean avatar image sean sean commented ·

I've just seen your comments about it being a Proven - this is a horrid format for keeping track of the conversation.

Could you confirm if the new installers have removed the Proven enclosure that outwardly had the red isolator along with the meters ?

You'll know that's what your dumps will have been previously connected to, I wonder if the new installers were aware of that enclosure also providing over voltage protection for the WT as well - we know that Provens are robust enough to run unloaded, but I would hope the new installation has not assumed that is an approved mode of operation.

0 Likes 0 ·
mikeb avatar image
mikeb answered ·

Hi


Just a question we’re they outback inverters or outback charge controllers?

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

desperatedan avatar image desperatedan commented ·

Inverters. But it's immaterial here, as they were used on our old system and it's the new one we're having problems with.

0 Likes 0 ·
mikeb avatar image mikeb desperatedan commented ·

Was just trying to understand how the wind turbine was controlled


So I could advise how to incorporate it on to the Victron kit


Regards

Mike

0 Likes 0 ·
desperatedan avatar image desperatedan mikeb commented ·

The wind turbine was controlled by the wind turbine controller that was supplied with it from Proven. That sent power to our house, our batteries, then the dump loads in that order, and it had three different relays which controlled those dump loads, so we had three dump loads! Then we had the Outback inverters as well. However, that's the old system, not the new one. The new one has done away with the wind turbine controller and replaced it and the inverters with the Quattro we now have.

0 Likes 0 ·
mikeb avatar image mikeb desperatedan commented ·

So have you the AC version of the wind turbine ?

0 Likes 0 ·
desperatedan avatar image desperatedan mikeb commented ·

Was just trying to understand how the wind turbine was controlled


So I could advise how to incorporate it on to the Victron kit


Sorry, I thought I'd explained but perhaps I wasn't clear. The turbine needed new blades and some other bits so while it was being refurbished the installer had it rewired to work at a different voltage, in order to make it compatible with this Victron kit. That means it's now not compatible with our old kit, so we've not got the old controller, or inverters, anything--just new Victron inverter/charger and some other bits.

0 Likes 0 ·
desperatedan avatar image
desperatedan answered ·

I've just read up the description of the Quattro inverter charger on the Victron website, and saw this:

"it can accept two AC inputs "

The installer told us we'd be able to add PV to our system with this kit, as it could handle multiple inputs. We've already got our wind turbine feeding into it, and our back up diesel generator, that's its two AC inputs used up, isn't it? So we can't add PV. So unless I'm missing something, that's another thing he told us that turns out to not be true.

I despair.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mikeb avatar image
mikeb answered ·

Hi

Do you think you require a installer to rectify the issue ?