question

pointer avatar image
pointer asked

I want to extend Pylontech 2000 Batterie to 500 Ah

Hello Team,

I have Installed 3 Phase Multiplus II System with and everything is working fine.

I using 6 x Pylontech 2000 it s working fine. But now i want to add another 4 x Pylontech 2000.

I have 300 Ah thats + 200 Ah I write the new number into the multiplus ok.

How do i make the bus connection and the jumper adjustment?

since the cerbogx does not recognize the pylontech 2000 with the recommended adjustments from the pylontech 2000 manual.

Multiplus-IIbattery chargingbattery
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
lifeingalicia avatar image
lifeingalicia answered ·
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pointer avatar image
pointer answered ·

essentially it says i have 10 Pylontech US2000 Batteries and can only use 8 or i need to get the LV hub?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

lifeingalicia avatar image lifeingalicia commented ·
As far as I know yes you should use a hub.

Probably also advisable regarding any waranty issues...

1 Bit addressing so just 8 on one can bus.

You could generate two banks with two can bus cables but can only see one in VRM

0 Likes 0 ·
klandos avatar image
klandos answered ·

At least with the “c” type pylontechs 16 modules are possible without LV Hub.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.