What is the Minimum Spacing between each of the Inverter in 3 x 10kw Victron Quattro Inverters on a 3 phase system

victron products
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
boekel avatar image
boekel answered ·

10cm is enough. But if that's a problem, you can also remove the top cover and mount them close to each other.

https://www.victronenergy.com/upload/documents/Manual-Quattro-5k-8k-10k-15K-100-100A-230V-(firmware-xxxx4xx)-EN-NL-FR-DE-ES-SE-IT.pdf

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Lothar Ledgerd avatar image
Lothar Ledgerd answered ·

Hi Ebrahim,

See my thread where I asked basically the same question. There have been some good answers but there doesn't appear to be any designs that optimise to limit temperature derating. In short, the recommendation was simply to install air conditioning or forced air if concerned.

https://community.victronenergy.com/questions/17555/cooling-for-9-x-quattro-15kva.html


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Paul B avatar image Paul B commented ·

Lother, keep in mind that most of your replies are NOT victron repling but other installers trying to be helpfull

0 Likes 0 ·