frederic avatar image
frederic asked
Expansion MEGA fuses
Hello
Will the 58V MEGA-fuse series expand?
I’m asking because:
The connection cables of Pylontech 48V are 4AWG, which is about 21QMM.
When I did my cable calculation, that’s about 63 Amps when in a cable tray with 40 degrees C.
That would mean it could charge/discharge 2 batteries at 25A each, 50A in total. A fuse of 60 Amps would be perfect in this case.
If I fuse this at 125A, the minimum available at 58V, the cable is not protected from 63A till 125A if a fault would occur.
So I hope an expansion will soon arrive.
thanks in advance
Frederic
fuses
Alexandra avatar image
Alexandra answered ·
@Frederic
Pylontec cables are different to other battery cables. Their insulation has a higher temperature rating, and a few other things that make them special.
Their 4AWG are rated for 120A. (It is stated in their manual). So the megas are perfect for them.
wkirby avatar image
wkirby answered ·
Indeed, I am using a 125A MEGA fuse with my Pylontch cables.
Like Alexandra said, the insulation is rated at a higher temperature and so the overall current rating is elevated, 105°C IIRC.
esa69 avatar image
esa69 answered ·
In the case that you use a 125A fuse then the cable will be the fuse, also I have seen tests with Victron Fuses where a fuse will blow not at 125Amps, but a much higher rate then 125 Amps and can be as high as 250Amps, so your 120Amp wire is now the fuse
I fully agree with Frederic to use a much lower fuse, like 63A or the next 80A Fuse and not the 125 Amp. And off course 48 volt version not the 12 or 24 volt versions
ahtrimble avatar image
ahtrimble answered ·
Problem is trying to find a 60a or 80a MEGA fuse for a 48v system. Anyone find a supplier yet?
hominidae avatar image hominidae commented ·
search fur MEGA fuses from littelfuse...they offer 60A/80A@70V as well as the other ranges.
Sources are Digi-Key (some are only available in large batches, not single pieces though) and I've seen these on ebay, too.
esa69 avatar image esa69 commented ·
Let me know if you need some, I have 60Amp 80Amp and 100Amp on stock with 70Volts, got them from a friend. Let me know how many you need and I will check price and how much we can send you (ps to where needs to be shipped?)
kevgermany avatar image
kevgermany answered ·
What people are missing is that the BMS in the lithium batteries will cut the output if overloaded.