I have 8x 12V Rolls S12 230AGM-RE in two 48V strings charged by 6x300W PV panels via EasySolar 48/5000.
The Victron Connect App factory Preset 2 seems fine except for the Absorb Voltage 14.4/57.6 whereas the Rolls user guide gives 14.7/58.8. (Float is same as the Victron Preset 2)
Should I edit the Preset 2 Absorb Voltage to 58.8 or use the Spiral AGM preset?
Is the higher Absorb setting necessary?
Is the Rolls S12 series a spiral AGM?
Thank you.
AGM Battery
kevgermany avatar image
kevgermany answered ·
Best to go to user defined and set the Rolls specified values there.
FRA avatar image
FRA answered ·
Rolls technical services says me that is mandatory to use 14.7v abs voltage and a fixed abs time with their formula 0.38*(capacity /charge current) in hours.
Or a end tail current of 2%, but only after one hour the tail current drop below 2% of capacity.
Rolls agm have a especially thick plates. More like spiral agm, but they are not spiral.
Common standard agm like victronenergy deep cycle have thinner plates respect to rolls agm.