this loading device has afaik 3 Outputs with 30A max. each. Is it possible to use two outputs from this device in parallel on one battery to increase charge current? E.g. to load a 200AH LiFePo4 Battery with 60A.
kind regards
itchako
Hi,
this loading device has afaik 3 Outputs with 30A max. each. Is it possible to use two outputs from this device in parallel on one battery to increase charge current? E.g. to load a 200AH LiFePo4 Battery with 60A.
kind regards
itchako
Whilst you can parallel the outputs from one device, you won't get any more current as the TOTAL current delivered is limited to 30A. If you need more current, then use 2 chargers in parallel.