BMV RS232 interface

Hi all,


I have a fully operational new system but currently without monitoring.

Multiplus 2 48v, BMV 700, automation system


The bmv has a 4 pin serial port on the rear.


5v, Rx, Tx, Gnd.


I have the victron cable 9pin rs232 to the BMV


In the said cable there is circuitry in the 9 pin end, the other end is sealed. see photo.


Questions


1; Are the electronics in the lead converting VE bus signals to RS232?

2; Is the output from the BMV’s Rx, Tx, & Gnd standard RS232 protocol or proprietary and only RS232 after the electronics?

3; Does pin 1 on the BMV need 5v or is it supplying 5v?

4; Is the Gnd common to signal & the 5v line?

Multiplus-IIBMV Battery Monitor48v batterybmv
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
wkirby avatar image
wkirby answered ·

1) No, there is no VE.Bus here. It is VE.Direct. That cable is converting VE.Direct (3.3V TTL) to RS232. It is isolated (Si8422 I think).

2) The output from a BMV is standard 3.3V TTL, not RS232. That cable converts TTL (3.3V or 5V) to RS232 (probably a MAX232 on the other side of that PCB???).

3) Pin 1 is supplying 3.3V (I think it is 10mA max). This voltage is needed to supply the BMV's side of the digital isolator (Si8422).

4) GND is common on the BMV side of the interface cable. It is isolated therefore GND is not common on the RS232 side.

10 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Martyn Duerden avatar image Martyn Duerden commented ·

Thanks for the reply.


Sorry, I did mean VE Direct!

The manual suggests its 5v not 3.3, are you saying VE direct operates as Rx,Tx & Ground? I had assumed it was CAN (Hi/Low) without Ground.


The issue at the moment is when plugged into an RS232 device there is no data stream, any thoughts?


Thanks

0 Likes 0 ·
wkirby avatar image wkirby ♦♦ Martyn Duerden commented ·

VE.Direct is TTL serial Rx, Tx and GND. It depends which manual you were reading. BMV's are 3.3V and MPPT's are 5V. The digital isolator is inherently a TTL Voltage level shifter too.

Now, on the 9pin side it's going to need to be powered in some way via the port. If you are expecting anything to come out of it between GND and Rx, then that won't happen on its own. The electronics need powering up on the RS232 side, probably by the DTR (pin 4) or RTS (pin 7) or something like that- difficult to say without seeing it in the flesh.

EDIT: I had another look at your picture, there is a track coming off pin 4 going to that giant capacitor?? That is most likely the pin powering the RS232 side of that converter.

0 Likes 0 ·
Martyn Duerden avatar image Martyn Duerden wkirby ♦♦ commented ·

That sounds like where we were


Pin 4 & 7 were powered up, in terms of grounding the RS232 side I had assumed it would be the housing, does this sound plausible?


Your edit...


So pin 4 & the shell or the rs232 gnd?


Will be back on it tomorrow!

0 Likes 0 ·
wkirby avatar image wkirby ♦♦ Martyn Duerden commented ·

RS232 GND (pin 5).

Sure, let's get on it tomorrow.

0 Likes 0 ·
Martyn Duerden avatar image Martyn Duerden Martyn Duerden commented ·

One other thing that strikes me, it will be expecting 3.3/5v on the 9 pin side too (as in not 10v for example)

0 Likes 0 ·
wkirby avatar image wkirby ♦♦ Martyn Duerden commented ·

No, it should be RS232 Voltage levels on the 9 pin side. It needs to interface with a computer (or USB serial thing) which will be at RS232 levels. I expect that there is a MAX232 or something like that on the other side of the PCB.

0 Likes 0 ·
mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ wkirby ♦♦ commented ·

Hi both,

“When using an external power supply to power DTR (pin 4) or RTS (pin 7), the minimum voltage is 5V, and maximum is 12V. Note that it is normally not necessary to use an external power supply for this: normal serial ports will either automatically drive DTR or RTS high. And if not that, than you can control those pins to be high from within the software.”


From:

https://www.victronenergy.com/live/vedirect_protocol:faq


Have you already studied that page? It explains all about 3v3 and 5v and ttl (and not canbus) and more.

0 Likes 0 ·
mvader (Victron Energy) avatar image mvader (Victron Energy) ♦♦ mvader (Victron Energy) ♦♦ commented ·

Ps: more than welcome to create an account there and better word it; in case its not clear

0 Likes 0 ·
Martyn Duerden avatar image Martyn Duerden mvader (Victron Energy) ♦♦ commented ·

Hi and thanks for the reply.


Our rs232 interface is Loxone (essentially a PLC) and only has Rx,Tx & Gnd terminals.


I have tried driving the DTR/RTS pins with 8v but cannot see any data stream.


Is there anyting that needs configuring on the BMV for it to ‘talk’ ?


Anything else you can think of?


Thanks

0 Likes 0 ·
joanspark avatar image joanspark Martyn Duerden commented ·
Did you ever get this working?
0 Likes 0 ·
wkirby avatar image
wkirby answered ·

The BMV just sends a data stream, there is no configuration. You can see the data pulsing out the back of the BMV with just a multimeter over pin 1 (GND) and 3 (Tx).