question

mysticmoer avatar image
mysticmoer asked

No Neutral Earth Bond Phoenix 24/800 Inverter

HI. I bought an Victron Phoenix Inverter 24/800 and none of the manuals that come with the inverter or that I can download, shows where I can bond neutral to earth.

The only way that I can see how to do it, is to move internal earth wire to neutral on output board. Would this be acceptable to do as it looks like there is provision made for it do be done.

I have attached some pics of output board.

Thanks


victron products
img-2847.jpg (1.5 MiB)
img-2851.jpg (580.4 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Mysticmoer

You are correct, the manual is incorrect, this is on the list to update...

So you'll have to make the N-E connection outside the unit unfortunately.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mysticmoer avatar image mysticmoer commented ·

Thanks Daniël.

0 Likes 0 ·
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·
Downloaded manual page 13:


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mysticmoer avatar image mysticmoer commented ·

I have also downloaded this manual and there are no circuits or boards with those labels inside.

0 Likes 0 ·

Related Resources

Additional resources still need to be added for this topic