We have an installation with 4 VE Direct MPPTs and an Octo GX. 3 of the 4 MPPTs are in a constant off state as shown in the photo. Second photo shows that they have an appropriate PV voltage and the battery SOC is only 30%.

We have tried switching the VE direct cables and also different VE direct ports on the Octo but it is always the same 3 units in the off state. The firmware was updated on all units and there is no error state on any of them.


Any ideas?



MPPT ControllersVE.Directgx device
mppt.png (53.5 KiB)
mppt-2.png (40.7 KiB)
4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

scott-simpson avatar image scott-simpson commented ·

I am the engineer who was on site when this problem occurred. On the remote console connection, under the device parameters for each of the MPPT’s the connection states USB. This should be VE Direct. I believe that the MPPT,s are on the USB Bus not the VE Direct Bus. Anyone have any ideas how to rectify this?

0 Likes 0 ·
scott-simpson avatar image scott-simpson commented ·

Here is a screenshot of one of the MPPT's

0 Likes 0 ·
mppt-usb.jpg (43.7 KiB)
wkirby avatar image wkirby ♦♦ scott-simpson commented ·

It will most likely be that (some) of the physical VE.Direct ports on the OctoGX talk to the CPU over a USB Bus rather than a native UART.
I don't know of many CPU / MPU chip sets which have that many native UARTs, so a USB Bus would be the only way to present that many serial (VE.Direct) ports to the outside world.
Some of the VE.Direct ports may connect to UARTs on the CPU, but I have not had the back off of an OctoGX, so I don't know for sure.

0 Likes 0 ·
scott-simpson avatar image scott-simpson wkirby ♦♦ commented ·

Thanks for the info. The first charger that was connected to the array is charging the battery and is on the USB bus. I disconnected all chargers (and reset factory defaults on each via Victron connect) then reconnected all except the one that was formerly charging. The same problem was there, none would charge, although they all showed battery and array voltage. I reconnected the one that was formerly charging and it worked fine. It seems that the octo has assigned a privilege to the working one, perhaps through its MAC address. But the main problem is that I need to get the chargers off the USB bus and on the VE.Direct bus.

0 Likes 0 ·
2 Answers
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Stevo07
Engineer logged on to the Octo, the mppt's state the 'remote input' is not ok, can it be the remote bridge connection is missing?


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

@Stevo07 & @Daniël Boekel (Victron Energy Staff)

Apologies, there was some site glitch and some of your follow up comments were lost. This is as best as I could recover. I have reported the bug.


@Stevo07 : This fixed the issue, many thanks! It was not immediately obvious that this should be checked, do you know where this info is contained?


@Daniël Boekel (Victron Energy Staff) : It is in the start up procedure in the MPPT manual, under cable connection sequence. It also comes connected from the factory, so someone has removed it.

0 Likes 0 ·
wkirby avatar image
wkirby answered ·

Is the charger enabled in Victronconnect?
A disabled charger will show an "Off" state in Venus.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

scott-simpson avatar image scott-simpson commented ·

All the chargers are enabled in victron connect.