question

kleszczewo avatar image
kleszczewo asked

100/20 or 100/30 controller?

I am contemplating the 100/20 or the 100/30 charge controller. The 100/20 has some built-in protections, which the 100/30 does not. How practical are those protections and can they be easily added to the 100/30 charge controller?


Thank you

MPPT Controllers
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

What protections are you thinking of?

The main difference I can think of is the load output terminals.

0 Likes 0 ·
kleszczewo avatar image kleszczewo Guy Stewart (Victron Community Manager) ♦♦ commented ·

Low voltage load disconnect

Battery reverse polarity

Output short circuit

0 Likes 0 ·
kleszczewo avatar image kleszczewo Guy Stewart (Victron Community Manager) ♦♦ commented ·

Doesn't the 100/20 have fuses that are user-replaceable, where the 100/30 needs to be sent in for replacement?

0 Likes 0 ·
1 Answer
wkirby avatar image
wkirby answered ·

Sure, but the 100/30 has lots of protection features that don't require a fuse, so that is why there is not one there.

"Over-temperature protection and power derating when temperature is high. PV short circuit and PV reverse polarity protection. PV reverse current protection."

Basically, have do do something really special to destroy this charge controller.
PV over voltage will destroy almost all MPPT's and probably reverse battery, and even a fuse would be too slow for this type of (user / installer) fault anyway.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources